Post Re: Official Insteon/Venstar Thermostat How To Thread
I'm not aware of any new end-user features.

_________________
Image


Sun May 20, 2012 5:58 pm
Profile WWW

Joined: Mar 31, 2008
Posts: 738
Post Caution with new V2.4 Rev 95 thermostats
I contacted Smarthome and they kindly sent me 5 replacement thermostats for my V2.0 units, and I had them installed for about a week. However, once installed they worked worse than the V2.0 units. For instance, I sent six up and then six down cool commands to each thermostat.They took forever to respond, just simply seeming to stall out. I thought some of my access points went bad. Then one of my appliance lincs, at some distance from the Indigo box, decided to not respond correctly. Finally they gave me a bogus temp value as noted below; the thermostat was reading 75 degrees.

I've put back the V2.0 units and the thermostats are working flawlessly again, with the series of up/down commands executing rapidly and accurately, and my appliance link is working again. Long story short, while it is possible they may have sent me a bad one or two, if my experience is representative, one might consider sticking with the V2.0 units.


Attachments:
IMG_0923.PNG
IMG_0923.PNG [ 68.35 KiB | Viewed 469 times ]
IMG_0922.PNG
IMG_0922.PNG [ 56.43 KiB | Viewed 469 times ]
Sat May 26, 2012 1:44 pm
Profile
Site Admin
User avatar

Joined: Jan 27, 2003
Posts: 11683
Location: Texas
Post Re: Caution with new V2.4 Rev 95 thermostats
Did you send the +6 and -6 setpoint commands back-to-back to all 5 thermostats without much delay between them? If so, I could see that causing quite a signal storm. The thermostats will broadcast out setpoint changes after they receive them, and if that broadcast occurred while Indigo was trying to send another thermostat a command (or a different thermostat was trying to do a broadcast) then I could see them getting in to a command collision war. That said, it should resolve itself without getting bogus temperature values.

What made the ApplianceLinc start working again? Did you just have to wait a couple of minutes for everything to settle down? And what did the Event Log look like during all of this?

Lastly, do you have the polling of the thermostats turned off in the Device dialog? They don't need to be polled, and the polling requires several INSTEON commands which will also increase the odds of collisions.

_________________
Image


Sat May 26, 2012 1:53 pm
Profile WWW

Joined: Mar 31, 2008
Posts: 738
Post Re: Caution with new V2.4 Rev 95 thermostats
matt (support) wrote:Did you send the +6 and -6 setpoint commands back-to-back to all 5 thermostats without much delay between them? If so, I could see that causing quite a signal storm. The thermostats will broadcast out setpoint changes after they receive them, and if that broadcast occurred while Indigo was trying to send another thermostat a command (or a different thermostat was trying to do a broadcast) then I could see them getting in to a command collision war. That said, it should resolve itself without getting bogus temperature values.


Yes. However, the rev 2.0 units work fine. Even when sending relatively slowly the other units bogged down. Indigo does not seem to be the issue here.

What made the ApplianceLinc start working again? Did you just have to wait a couple of minutes for everything to settle down? And what did the Event Log look like during all of this?


Can't explain the ApplianceLinc except that it stopped responding when these adapters were installed and now seems OK. A couple of event logs showing a series of "no acknowledgement" and also "checksum invalid" is below. Note that the cool set point is repeatedly set to 82 degrees????

Code: Select all
2012-05-21 23:56:14   Error   "Thermostat Main Bedrooms" set heat setpoint to 64.0; send failed (no acknowledgment)
2012-05-21 23:56:21   Error   "Thermostat Main Bedrooms" set cool setpoint to 83.0; send failed (no acknowledgment)
2012-05-21 23:56:29   Error   "Thermostat Main Bedrooms" set heat setpoint to 63.0; send failed (no acknowledgment)
2012-05-21 23:56:30   Sent INSTEON   "Thermostat Main Bedrooms" set cool setpoint to 82.0
2012-05-21 23:56:32   Received INSTEON   "Thermostat Main Bedrooms" cool setpoint changed to 82.0
2012-05-21 23:56:33   Received INSTEON   "Thermostat Main Bedrooms" cool setpoint changed to 82.0
2012-05-21 23:56:34   Received INSTEON   "Thermostat Main Bedrooms" cool setpoint changed to 82.0
2012-05-21 23:56:34   Received INSTEON   "Thermostat Main Bedrooms" cool setpoint changed to 82.0
2012-05-21 23:56:42   Error   "Thermostat Main Bedrooms" set heat setpoint to 62.0; send failed (no acknowledgment)
2012-05-21 23:56:49   Error   "Thermostat Main Bedrooms" set cool setpoint to 81.0; send failed (no acknowledgment)
2012-05-21 23:56:53   Error   "Thermostat Main Bedrooms" set heat setpoint to 61.0; failed (illegal value in command)
2012-05-21 23:57:00   Error   "Thermostat Main Bedrooms" set cool setpoint to 80.0; send failed (no acknowledgment)
2012-05-21 23:57:08   Error   "Thermostat Main Bedrooms" set cool setpoint to 79.0; send failed (no acknowledgment)
2012-05-21 23:57:15   Error   "Thermostat Main Bedrooms" set heat setpoint to 60.0; send failed (no acknowledgment)
2012-05-21 23:57:23   Error   "Thermostat Main Bedrooms" set heat setpoint to 59.0; send failed (no acknowledgment)
2012-05-21 23:57:24   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 78.0
2012-05-21 23:57:32   Error   "Thermostat Main Bedrooms" set cool setpoint to 78.0; send failed (no acknowledgment)
2012-05-21 23:57:39   Error   "Thermostat Main Bedrooms" set cool setpoint to 77.0; send failed (no acknowledgment)
2012-05-21 23:57:42   Sent INSTEON   "Thermostat Main Bedrooms" set heat setpoint to 58.0
2012-05-21 23:57:42   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 85.0
2012-05-21 23:57:43   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 58.0
2012-05-21 23:57:44   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 58.0
2012-05-21 23:57:44   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 58.0
2012-05-21 23:57:45   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 58.0
2012-05-21 23:57:46   Received INSTEON   "Thermostat Fam Study" cool setpoint changed to 85.0
2012-05-21 23:57:53   Error   "Thermostat Fam Study" set heat setpoint to 59.0; send failed (no acknowledgment)
2012-05-21 23:58:01   Error   "Thermostat Main Bedrooms" set cool setpoint to 81.0; send failed (no acknowledgment)
2012-05-21 23:58:08   Error   "Thermostat Main Bedrooms" set heat setpoint to 57.0; send failed (no acknowledgment)
2012-05-21 23:58:16   Error   "Thermostat Main Bedrooms" set cool setpoint to 80.0; send failed (no acknowledgment)
2012-05-21 23:58:23   Action Group   aStatus Update A/C
2012-05-21 23:58:23   Error   "Thermostat Main Bedrooms" set heat setpoint to 57.0; send failed (no acknowledgment)
2012-05-21 23:58:31   Error   "Thermostat Main Bedrooms" set heat setpoint to 56.0; send failed (no acknowledgment)
2012-05-21 23:58:34   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 79.0
2012-05-21 23:58:35   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 79.0
2012-05-21 23:58:35   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 79.0
2012-05-21 23:58:36   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 79.0
2012-05-21 23:58:36   Received INSTEON   "Thermostat Main Bedrooms" temperature changed to 79.0
2012-05-21 23:58:44   Error   "Thermostat Main Bedrooms" set cool setpoint to 79.0; send failed (no acknowledgment)
2012-05-21 23:58:51   Error   "Thermostat Main Bedrooms" set heat setpoint to 55.0; send failed (no acknowledgment)
2012-05-21 23:58:59   Error   "Thermostat Main Bedrooms" set cool setpoint to 78.0; send failed (no acknowledgment)
2012-05-21 23:58:59   Sent INSTEON   "Thermostat Fam Room" mode request (received: auto on)
2012-05-21 23:59:00   Sent INSTEON   "Thermostat Fam Room" temperature request (received: 79.0)
2012-05-21 23:59:00   Sent INSTEON   "Thermostat Fam Room" humidity request (received: 43.0)
2012-05-21 23:59:04   Sent INSTEON   "Thermostat Fam Room" setpoint request (received: heat 58.0, cool 84.0)
2012-05-21 23:59:04   Sent INSTEON   "Thermostat Fam Study" mode request (received: auto on)
2012-05-21 23:59:04   Sent INSTEON   "Thermostat Fam Study" temperature request (received: 78.0)
2012-05-21 23:59:05   Sent INSTEON   "Thermostat Fam Study" humidity request (received: 47.0)
2012-05-21 23:59:08   Sent INSTEON   "Thermostat Fam Study" setpoint request (received: heat 67.0, cool 85.0)
2012-05-21 23:59:08   Sent INSTEON   "Thermostat GameRm" mode request (received: auto on)
2012-05-21 23:59:08   Sent INSTEON   "Thermostat GameRm" temperature request (received: 78.0)
2012-05-21 23:59:10   Sent INSTEON   "Thermostat GameRm" humidity request (received: 47.0)
2012-05-21 23:59:14   Sent INSTEON   "Thermostat GameRm" setpoint request (received: heat 60.0, cool 84.0)
2012-05-21 23:59:16   Sent INSTEON   "Thermostat Main Bedrooms" mode request (received: auto on)
2012-05-21 23:59:22   Error   "Thermostat Main Bedrooms" temperature request; send failed (no acknowledgment)
2012-05-21 23:59:28   Error   "Thermostat Main Bedrooms" humidity request; send failed (no acknowledgment)
2012-05-21 23:59:35   Error   "Thermostat Main Bedrooms" setpoint request; send failed (no acknowledgment)
2012-05-21 23:59:35   Sent INSTEON   "Thermostat MBR" mode request (received: auto on)
2012-05-21 23:59:36   Sent INSTEON   "Thermostat MBR" temperature request (received: 75.0)
2012-05-21 23:59:37   Sent INSTEON   "Thermostat MBR" humidity request (received: 34.0)
2012-05-21 23:59:40   Sent INSTEON   "Thermostat MBR" setpoint request (received: heat 63.0, cool 74.0)
2012-05-21 23:59:47   Error   "Thermostat Main Bedrooms" set cool setpoint to 77.0; send failed (no acknowledgment)
2012-05-21 23:59:49   Sent INSTEON   "Thermostat Main Bedrooms" set heat setpoint to 54.0
2012-05-21 23:59:52   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 54.0
2012-05-21 23:59:53   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 54.0
2012-05-21 23:59:53   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 54.0


2012-05-23 22:11:37   Error   "Thermostat Main Bedrooms" set cool setpoint to 75.0; failed (checksum invalid)
2012-05-23 22:11:38   Sent INSTEON   "Thermostat Main Bedrooms" set heat setpoint to 64.0
2012-05-23 22:11:42   Received INSTEON   "GamPsgWy Master" on
2012-05-23 22:11:42   Received INSTEON   "Backyard Big Lts Passageway Slave" on
2012-05-23 22:11:42   Trigger   Outdoor Lts Back PsgWy On Timer
2012-05-23 22:11:43   Error   "Thermostat MBR" set cool setpoint to 83.0; failed (checksum invalid)
2012-05-23 22:11:44   Error   "Thermostat MBR" set heat setpoint to 59.0; failed (checksum invalid)
2012-05-23 22:11:45   Sent INSTEON   "Backyard Big Lts Fam Rm Switch" on to 85
2012-05-23 22:11:45   Trigger   Lights BackYard Variable
2012-05-23 22:11:45   Sent INSTEON   "Backyard Big Lts Passageway Slave" on to 100
2012-05-23 22:11:46   Received INSTEON   "Game Rm Front FP Lts" on
2012-05-23 22:11:46   Error   "Thermostat MBR" set heat setpoint to 58.0; failed (checksum invalid)
2012-05-23 22:11:47   Sent INSTEON   "Thermostat MBR" set cool setpoint to 82.0
2012-05-23 22:11:48   Sent INSTEON   "Thermostat MBR" set heat setpoint to 57.0
2012-05-23 22:11:49   Sent INSTEON   "Thermostat MBR" set cool setpoint to 81.0
2012-05-23 22:11:49   Sent INSTEON   "Thermostat MBR" set heat setpoint to 56.0
2012-05-23 22:11:50   Sent INSTEON   "Thermostat MBR" set cool setpoint to 80.0
2012-05-23 22:11:51   Received INSTEON   "Thermostat MBR" cool setpoint changed to 80.0
2012-05-23 22:11:56   Received INSTEON   "Thermostat MBR" heat setpoint changed to 55.0
2012-05-23 22:12:03   Error   "Thermostat MBR" set heat setpoint to 55.0; send failed (no acknowledgment)
2012-05-23 22:12:04   Sent INSTEON   "Thermostat MBR" set cool setpoint to 79.0
2012-05-23 22:12:04   Sent INSTEON   "Thermostat MBR" set cool setpoint to 78.0
2012-05-23 22:12:06   Received INSTEON   "Thermostat MBR" cool setpoint changed to 79.0
2012-05-23 22:12:11   Received INSTEON   "Thermostat MBR" cool setpoint changed to 78.0
2012-05-23 22:12:18   Error   "Thermostat MBR" set heat setpoint to 54.0; send failed (no acknowledgment)
2012-05-23 22:12:20   Received INSTEON   "Thermostat MBR" cool setpoint changed to 77.0
2012-05-23 22:12:24   Received INSTEON   "Thermostat MBR" on (button 1)
2012-05-23 22:12:24   Error   "Thermostat MBR" set cool setpoint to 77.0; failed
2012-05-23 22:12:25   Error   "Thermostat MBR" set heat setpoint to 53.0; failed (checksum invalid)
2012-05-23 22:12:25   Sent INSTEON   "Thermostat MBR" set cool setpoint to 79.0
2012-05-23 22:12:26   Sent INSTEON   "Thermostat MBR" set heat setpoint to 54.0
2012-05-23 22:12:28   Received INSTEON   "Thermostat MBR" off (button 1)
2012-05-23 22:12:30   Received INSTEON   "Thermostat MBR" cool setpoint changed to 79.0
2012-05-23 22:12:34   Received INSTEON   "Thermostat MBR" heat setpoint changed to 54.0
2012-05-23 22:12:35   Sent INSTEON   "Thermostat MBR" set cool setpoint to 78.0
2012-05-23 22:12:36   Sent INSTEON   "Thermostat MBR" set heat setpoint to 53.0
2012-05-23 22:12:36   Sent INSTEON   "Thermostat MBR" set heat setpoint to 52.0
2012-05-23 22:12:37   Sent INSTEON   "Thermostat MBR" set cool setpoint to 77.0
2012-05-23 22:12:38   Error   "Thermostat MBR" set heat setpoint to 51.0; failed (checksum invalid)
2012-05-23 22:12:40   Sent INSTEON   "Thermostat MBR" set cool setpoint to 76.0
2012-05-23 22:12:41   Sent INSTEON   "Thermostat MBR" set heat setpoint to 50.0
2012-05-23 22:12:42   Sent INSTEON   "Thermostat MBR" set cool setpoint to 75.0
2012-05-23 22:12:43   Sent INSTEON   "Thermostat MBR" set heat setpoint to 49.0
2012-05-23 22:12:44   Sent INSTEON   "Thermostat MBR" set cool setpoint to 74.0
2012-05-23 22:12:45   Received INSTEON   "Thermostat MBR" cool setpoint changed to 74.0
2012-05-23 22:12:49   Received INSTEON   "Thermostat MBR" heat setpoint changed to 49.0
2012-05-23 22:12:50   Received INSTEON   "Thermostat MBR" heat setpoint changed to 49.0
2012-05-23 22:13:09   Sent INSTEON   "Thermostat Main Bedrooms" set cool setpoint to 74.0
2012-05-23 22:13:10   Sent INSTEON   "Thermostat Main Bedrooms" set heat setpoint to 63.0
2012-05-23 22:13:11   Received INSTEON   "Thermostat Main Bedrooms" cool setpoint changed to 74.0
2012-05-23 22:13:15   Received INSTEON   "Thermostat Main Bedrooms" heat setpoint changed to 63.0
2012-05-23 22:13:17   Action Group   aStatus Update A/C
2012-05-23 22:13:17   Sent INSTEON   "Thermostat Fam Room" mode request (received: auto on)
2012-05-23 22:13:17   Sent INSTEON   "Thermostat Fam Room" temperature request (received: 77.0)
2012-05-23 22:13:20   Sent INSTEON   "Thermostat Fam Room" humidity request (received: 37.0)
2012-05-23 22:13:23   Sent INSTEON   "Thermostat Fam Room" setpoint request (received: heat 67.0, cool 76.0)
2012-05-23 22:13:24   Sent INSTEON   "Thermostat Fam Study" mode request (received: auto on)
2012-05-23 22:13:24   Sent INSTEON   "Thermostat Fam Study" temperature request (received: 77.0)
2012-05-23 22:13:26   Sent INSTEON   "Thermostat Fam Study" humidity request (received: 42.0)
2012-05-23 22:13:28   Sent INSTEON   "Thermostat Fam Study" setpoint request (received: heat 67.0, cool 76.0)
2012-05-23 22:13:34   Error   "Thermostat GameRm" mode request; send failed (no acknowledgment)
2012-05-23 22:13:40   Error   "Thermostat GameRm" temperature request; send failed (no acknowledgment)
2012-05-23 22:13:47   Error   "Thermostat GameRm" humidity request; send failed (no acknowledgment)
2012-05-23 22:13:53   Error   "Thermostat GameRm" setpoint request; send failed (no acknowledgment)




The Event Log for the good thermostats is below. They work quickly and accurately:

Code: Select all
2012-05-26 09:09:20   Sent INSTEON   "Thermostat MBR" set cool setpoint to 77.0
2012-05-26 09:09:20   Sent INSTEON   "Thermostat MBR" set heat setpoint to 66.0
2012-05-26 09:09:21   Sent INSTEON   "Thermostat MBR" set cool setpoint to 78.0
2012-05-26 09:09:21   Sent INSTEON   "Thermostat MBR" set heat setpoint to 67.0
2012-05-26 09:09:22   Sent INSTEON   "Thermostat MBR" set cool setpoint to 79.0
2012-05-26 09:09:22   Sent INSTEON   "Thermostat MBR" set heat setpoint to 68.0
2012-05-26 09:09:23   Received INSTEON   "Thermostat Fam Room" humidity changed to 41.0
2012-05-26 09:09:24   Sent INSTEON   "Thermostat MBR" set cool setpoint to 80.0
2012-05-26 09:09:24   Sent INSTEON   "Thermostat MBR" set heat setpoint to 69.0
2012-05-26 09:09:25   Sent INSTEON   "Thermostat MBR" set cool setpoint to 81.0
2012-05-26 09:09:25   Sent INSTEON   "Thermostat MBR" set heat setpoint to 70.0
2012-05-26 09:09:27   Received INSTEON   "Thermostat MBR" cool setpoint changed to 81.0
2012-05-26 09:09:28   Sent INSTEON   "Thermostat MBR" set cool setpoint to 80.0
2012-05-26 09:09:29   Sent INSTEON   "Thermostat MBR" set heat setpoint to 69.0
2012-05-26 09:09:29   Sent INSTEON   "Thermostat MBR" set cool setpoint to 79.0
2012-05-26 09:09:31   Sent INSTEON   "Thermostat MBR" set heat setpoint to 68.0
2012-05-26 09:09:31   Sent INSTEON   "Thermostat MBR" set cool setpoint to 78.0
2012-05-26 09:09:31   Sent INSTEON   "Thermostat MBR" set heat setpoint to 67.0
2012-05-26 09:09:32   Sent INSTEON   "Thermostat MBR" set cool setpoint to 77.0
2012-05-26 09:09:32   Sent INSTEON   "Thermostat MBR" set heat setpoint to 66.0
2012-05-26 09:09:33   Sent INSTEON   "Thermostat MBR" set cool setpoint to 76.0
2012-05-26 09:09:34   Sent INSTEON   "Thermostat MBR" set heat setpoint to 65.0
2012-05-26 09:09:38   Received INSTEON   "Thermostat MBR" cool setpoint changed to 76.0
2012-05-26 09:09:40   Received INSTEON   "Thermostat Fam Study" humidity changed to 44.0
2012-05-26 09:09:41   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 85.0
2012-05-26 09:09:41   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 61.0
2012-05-26 09:09:42   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 86.0
2012-05-26 09:09:42   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 62.0
2012-05-26 09:09:43   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 87.0
2012-05-26 09:09:43   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 63.0
2012-05-26 09:09:44   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 88.0
2012-05-26 09:09:44   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 64.0
2012-05-26 09:09:44   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 89.0
2012-05-26 09:09:45   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 65.0
2012-05-26 09:09:46   Received INSTEON   "Thermostat GameRm" cool setpoint changed to 89.0
2012-05-26 09:09:49   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 88.0
2012-05-26 09:09:50   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 64.0
2012-05-26 09:09:50   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 87.0
2012-05-26 09:09:51   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 63.0
2012-05-26 09:09:51   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 86.0
2012-05-26 09:09:52   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 62.0
2012-05-26 09:09:52   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 85.0
2012-05-26 09:09:53   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 61.0
2012-05-26 09:09:53   Sent INSTEON   "Thermostat GameRm" set cool setpoint to 84.0
2012-05-26 09:09:54   Sent INSTEON   "Thermostat GameRm" set heat setpoint to 60.0
2012-05-26 09:09:57   Received INSTEON   "Thermostat GameRm" cool setpoint changed to 84.0
2012-05-26 09:10:00   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 77.0
2012-05-26 09:10:00   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 66.0
2012-05-26 09:10:01   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 78.0
2012-05-26 09:10:01   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 67.0
2012-05-26 09:10:01   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 79.0
2012-05-26 09:10:02   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 68.0
2012-05-26 09:10:02   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 80.0
2012-05-26 09:10:03   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 69.0
2012-05-26 09:10:03   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 81.0
2012-05-26 09:10:04   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 70.0
2012-05-26 09:10:06   Received INSTEON   "Thermostat Fam Study" off (button 1)
2012-05-26 09:10:07   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 80.0
2012-05-26 09:10:07   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 69.0
2012-05-26 09:10:07   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 79.0
2012-05-26 09:10:08   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 68.0
2012-05-26 09:10:08   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 78.0
2012-05-26 09:10:09   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 67.0
2012-05-26 09:10:09   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 77.0
2012-05-26 09:10:10   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 66.0
2012-05-26 09:10:10   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 65.0
2012-05-26 09:10:11   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 76.0
2012-05-26 09:10:16   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 77.0
2012-05-26 09:10:16   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 66.0
2012-05-26 09:10:17   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 78.0
2012-05-26 09:10:17   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 67.0
2012-05-26 09:10:18   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 79.0
2012-05-26 09:10:18   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 68.0
2012-05-26 09:10:19   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 80.0
2012-05-26 09:10:19   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 69.0
2012-05-26 09:10:20   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 81.0
2012-05-26 09:10:20   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 70.0
2012-05-26 09:10:21   Received INSTEON   "Thermostat Fam Room" cool setpoint changed to 81.0
2012-05-26 09:10:22   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 80.0
2012-05-26 09:10:22   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 69.0
2012-05-26 09:10:23   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 79.0
2012-05-26 09:10:23   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 68.0
2012-05-26 09:10:24   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 78.0
2012-05-26 09:10:24   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 67.0
2012-05-26 09:10:25   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 77.0
2012-05-26 09:10:25   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 66.0
2012-05-26 09:10:26   Sent INSTEON   "Thermostat Fam Room" set cool setpoint to 76.0
2012-05-26 09:10:26   Sent INSTEON   "Thermostat Fam Room" set heat setpoint to 65.0
2012-05-26 09:10:30   Received INSTEON   "Thermostat Fam Room" cool setpoint changed to 76.0
2012-05-26 09:10:31   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 77.0
2012-05-26 09:10:32   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 66.0
2012-05-26 09:10:32   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 78.0
2012-05-26 09:10:33   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 67.0
2012-05-26 09:10:33   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 79.0
2012-05-26 09:10:34   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 68.0
2012-05-26 09:10:34   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 69.0
2012-05-26 09:10:35   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 80.0
2012-05-26 09:10:35   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 81.0
2012-05-26 09:10:36   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 70.0
2012-05-26 09:10:37   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 80.0
2012-05-26 09:10:38   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 69.0
2012-05-26 09:10:38   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 79.0
2012-05-26 09:10:39   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 68.0
2012-05-26 09:10:39   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 67.0
2012-05-26 09:10:40   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 78.0
2012-05-26 09:10:40   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 77.0
2012-05-26 09:10:40   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 66.0
2012-05-26 09:10:41   Sent INSTEON   "Thermostat Fam Study" set cool setpoint to 76.0
2012-05-26 09:10:41   Sent INSTEON   "Thermostat Fam Study" set heat setpoint to 65.0


Lastly, do you have the polling of the thermostats turned off in the Device dialog? They don't need to be polled, and the polling requires several INSTEON commands which will also increase the odds of collisions.


Polling is turned off. As soon as I replaced them with the old units, the thermostats all functioned normally.


Last edited by hamw on Sat May 26, 2012 2:41 pm, edited 1 time in total.



Sat May 26, 2012 2:31 pm
Profile
Site Admin
User avatar

Joined: Jan 27, 2003
Posts: 11683
Location: Texas
Post Re: Caution with new V2.4 Rev 95 thermostats
Have you sent them back to Smarthome? They need to look into this. It looks like they are getting into a bad repeating state in this case. If you can reproduce the problem they will likely be interested in the details.

_________________
Image


Sat May 26, 2012 2:34 pm
Profile WWW

Joined: Mar 31, 2008
Posts: 738
Post Re: Official Insteon/Venstar Thermostat How To Thread
Have not yet sent them back, but I agree they will want to know. I also appended the prior post with a log showing "checksum invalid" errors.


Sat May 26, 2012 2:42 pm
Profile

Joined: Oct 28, 2007
Posts: 299
Post Re: Official Insteon/Venstar Thermostat How To Thread
Has anyone else upgraded to the new 2.4R stat adapter? Success, Failure?


Tue May 29, 2012 11:06 am
Profile

Joined: Oct 28, 2007
Posts: 299
Post Re: Official Insteon/Venstar Thermostat How To Thread
No one has installed the recalled adapter yet? Really?


Thu May 31, 2012 4:44 pm
Profile

Joined: May 25, 2009
Posts: 95
Post Re: Official Insteon/Venstar Thermostat How To Thread
SmartHome sent me two Venstar/INSTEON 2.4R replacement modules a few weeks ago. One of them is worse than any of the previous ones. I have had to pull it and replug it three times in about 3 weeks. It fails to respond and apparently clogs the wireless causing errors with communication to many other INSTEON devices. Oddly, this is the same thermostat that had the most problem over the last couple years. I wonder if the problem is in the Venstar instead of the INSTEON module.


Sat Jun 02, 2012 5:30 pm
Profile

Joined: Mar 31, 2008
Posts: 738
Post Re: Official Insteon/Venstar Thermostat How To Thread
Try swapping modules and thermostats and see if behavior is changed?


Sat Jun 02, 2012 5:42 pm
Profile
Site Admin
User avatar

Joined: Mar 19, 2008
Posts: 6642
Location: Austin, Texas
Post Re: Official Insteon/Venstar Thermostat How To Thread
Agreed - swap the thermostats but leave the adapter in the same location and see if the problem follows the thermostat or stays with the adaptor.

_________________
Jay (Indigo Support)
Image


Sat Jun 02, 2012 9:27 pm
Profile WWW

Joined: Mar 31, 2008
Posts: 738
Post Re: Official Insteon/Venstar Thermostat How To Thread
Am currently using the v2.0 thermostat adapters. I've been getting repetitive sends from a couple of the adapters:
Code: Select all
4Jul, 2012 9:02:09 PM
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0

4Jul, 2012 9:03:17 PM
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0
  Received INSTEON                "Thermostat Fam Room" on (button 1)
  Received INSTEON                "Thermostat Fam Room" temperature changed to 78.0

4Jul, 2012 9:04:25 PM
  Received INSTEON                "Thermostat GameRm" humidity changed to 27.0
  Received INSTEON                "Thermostat Fam Room" humidity changed to 36.0

4Jul, 2012 9:05:32 PM
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0

4Jul, 2012 9:06:38 PM
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Fam Room" humidity changed to 35.0

4Jul, 2012 9:07:47 PM
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 37.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 37.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 37.0
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 37.0

4Jul, 2012 9:08:53 PM
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 38.0
  Received INSTEON                "Thermostat Fam Room" humidity changed to 34.0

4Jul, 2012 9:11:08 PM
  Received INSTEON                "Thermostat Fam Room" temperature changed to 77.0

4Jul, 2012 9:11:28 PM
  Received INSTEON                "Thermostat GameRm" on (button 1)

4Jul, 2012 9:12:04 PM
  Received INSTEON                "Thermostat GameRm" temperature changed to 80.0

4Jul, 2012 9:13:18 PM
  Received INSTEON                "Thermostat Fam Room" humidity changed to 33.0

4Jul, 2012 9:14:15 PM
  Received INSTEON                "Thermostat GameRm" humidity changed to 29.0
  Received INSTEON                "Thermostat Fam Room" humidity changed to 34.0

4Jul, 2012 9:16:25 PM
  Received INSTEON                "Thermostat GameRm" temperature changed to 79.0
  Received INSTEON                "Thermostat Main Bedrooms" on (button 1)

4Jul, 2012 9:17:31 PM
  Received INSTEON                "Thermostat GameRm" humidity changed to 28.0

4Jul, 2012 9:18:33 PM
  Received INSTEON                "Thermostat Main Bedrooms" humidity changed to 40.0

4Jul, 2012 9:19:47 PM
  Received INSTEON                "Thermostat Fam Room" humidity ch


Have you seen this before, or does it sound like a Venstar issue?


Wed Jul 04, 2012 9:02 pm
Profile
Site Admin
User avatar

Joined: Mar 19, 2008
Posts: 6642
Location: Austin, Texas
Post Re: Official Insteon/Venstar Thermostat How To Thread
What Indigo version are you using?

_________________
Jay (Indigo Support)
Image


Thu Jul 05, 2012 9:25 am
Profile WWW

Joined: Mar 31, 2008
Posts: 738
Post Re: Official Insteon/Venstar Thermostat How To Thread
5.1.3 but it has been doing it for a while.


Thu Jul 05, 2012 7:19 pm
Profile
Site Admin
User avatar

Joined: Mar 19, 2008
Posts: 6642
Location: Austin, Texas
Post Re: Official Insteon/Venstar Thermostat How To Thread
Hmmm. I believe Matt worked around a bug in the firmware that caused multiple duplicate messages but that was several versions ago. What's the firmware version number on those?

_________________
Jay (Indigo Support)
Image


Thu Jul 05, 2012 7:45 pm
Profile WWW
Display posts from previous:  Sort by  
Reply to topic   [ 322 posts ]  Go to page: Previous  1 ... 16, 17, 18, 19, 20, 21, 22  Next

Who is online

Users browsing this forum: Google Feedfetcher and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group.   Template designed by STSoftware.